首页 > 国外线缆
[问题求助] THW TW THHN THWN XHHW 这些叫法是什么啊
P:2012-12-06 09:52:25
THW TW THHN THWN  XHHW 这些叫法是什么啊 , 大侠指点
tubular strander with prestressing - 预加压式管式绞线机 (0) 投诉
P:2012-12-06 10:28:14
电线的型号
quadding equipment - 四线组绞制设备 (0) 投诉
P:2012-12-06 10:58:22
查核一下UL83,里面应该有
bracket wheel up-and-down plate - 托轮升降板(印字机的) (0) 投诉
P:2012-12-28 09:05:13
UL83里面的线规,N代表尼龙。W代表防水户外用。
powder overspray input - 粉末过喷进料口 (0) 投诉
P:2012-12-29 14:14:30
那X 呢
four-wire side chute - 四线实线电路 (0) 投诉
P:2012-12-29 16:21:07
PRODUCT TYPES
Thermoplastic-insulated wire is rated 600 V and is designated as follows:
TW — Indicates a single conductor having flame-retardant, moisture-resistant thermoplastic insulation. The wire is rated 60°C wet or dry.
THHN — Indicates a single conductor having flame-retardant and heat-resistant thermoplastic insulation with a jacket of extruded nylon or equivalent material. The wire is rated 90°C dry only.
THW — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation. The wire is rated 75°C wet or dry.
THW-2 — Same as THW except that the wire is rated 90°C wet or dry.
THHW — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation. The wire is rated 90°C dry and 75°C wet.
THWN — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation with a jacket of extruded nylon or equivalent material. The wire is rated 75°C wet or dry. THWN wire suitable for exposure to mineral oil and to liquid gasoline and gasoline vapors at ordinary ambient temperature is marked "Gasoline and Oil Resistant I" if suitable for exposure to mineral oil at 60°C, or "Gasoline and Oil Resistant II" if the compound is suitable for exposure to mineral oil at 75°C. Gasoline resistant wire has been tested at 23°C when immersed in gasoline. It is considered inherently resistant to gasoline vapors within the limits of the temperature rating.
THWN-2 — Same as THWN except that the wire is rated 90°C wet or dry.
underfloor raceway - 地下电缆管道;地板下的配线 (3) 投诉
P:2012-12-29 16:22:12
XHHW 交联聚乙烯绝缘, 聚氯乙烯护套控制电缆
rod - 杆,线杆,棒材 (0) 投诉
P:2013-01-15 14:41:05
回复的比较全面 <div>不知道这些都是在哪里查到的呢</div>
error ratio - 差错率,误码率 (0) 投诉
P:2014-06-30 16:59:30
H 在這裡什麼意思?
machinability - 可加工性,机械加工性,机制佳 (0) 投诉
P:2026-09-07 14:17:04
kable:
那X 呢
看UL 44标准
delivery test - 出厂试验 (0) 投诉